Sounds to me that the emergency stops are wired in parallel. they should be wired in series. so Peter is right, check your wiring.then only need to pull one out
It is not tearing it apart, it's just confirming that the fault is in the board.i am not going to tear it apart
And the doc on Checking Optocouplers just checks the voltages around the opto to determine where the fault is.Testing procedure for the Estop Input
- Opto No: 38 is used for the E-Stop signal.
- Remove the wire connected to Estop 2.
- Go to the F1 screen and make sure the Estop input shows LOW and is not inverted.
- Test the optocoupler by connecting the +ve of the MASSO power supply through a 5.6K resistor to the EStop2 input
- On the F1 screen, you should see the input change from LOW to HIGH.
- If the input changes from one state to the other the optocoupler is ok and does not need replacing.
I only suggested you carry out the checks listed in the docs, so that you are ready with answers to prove that they are at fault.i have a ticket started with them ty