Hoping for feedback on my CNC controller wiring diagram

tmtoronto

TMToronto
Understanding that my last posts required a great deal of time to digest, I thought I would try one last time to get forum feedback on the power wiring for my controller enclosure. It is hand drawn, and uses words instead of electrical symbols, but my hope is that those with experience will catch any glaring errors - I really do not want to compromise my Masso, MX4660 driver, ... or my home.

A few quick notes:

I have a power module which fuses both Line and Neutral, currently with 10A (came with unit), and it also serves as an on/off switch and EMF filter

I have 5, 12, 2X24, and 48VDC power supplies, dedicating 24VDC to the Masso and 48VDC to the MX4660 driver. The other VDC will give options for adding sensors, relays...

I have the grounds and common(-) all terminating in their own connected terminal blocks.

I have the Masso POS+ on a 1A fuse, and the other 24VDC also, for now fused the same but the amperage could change depending on future loads

I have both the POS- and Common(-) of the 48VDC PSU fused, at the moment with 15A fuses, as well as a 63V/2200uF capacitor to help dissipate back EMF

I have several terminal blocks joined using jumpers, which can be seen in the drawing as small horizontal rectangles across the terminal blocks.

I understand the time commitment required to provide feedback, but it would very much give me greater peace of mind to actually turn on the power and run my Masso for the first time.

Thank you
 

Attachments

  • Controller-wiring-drawing.jpeg
    Controller-wiring-drawing.jpeg
    1.7 MB · Views: 42

evermech

evermech
Well that looks pretty nice to me. Plenty of power options and the fuses are there where needed. I m not sure about all of the grounds going to a terminal block and then to your ground lug. If the terminal blocks are the kind that ground to the Din rail each separately then I would think it would be good. You will need someone else s opinion on that one.

Guy
 

tmtoronto

TMToronto
Thank you very much for the feedback, I really appreciate it.

These are proper ground terminal blocks, and as you said they do contact the DIN rail and therefore are already grounded to the mounting plate, and through the screws as well. I wanted the addition of the ground lug as the first place the mains ground attaches so that I know the mounting plate will always have a connected ground, regardless of what happens downstream. When in the enclosure cabinet, the mounting plate will also connected/grounded to the enclosure door at the other end - not shown in this diagram or the photos in my previous build posts.
 