How to wire VFD to Masso Controller
stover99
stover99
Thanks for any advice you can give. I have a VFD that I am trying wire to the Masso G3 controller. I am not sure which pins to use for the Masso spindle control output and what to use for the VFD. I have looked over the documentation and videos and have not been able to find the best configuration for my inverter. Your help would be appreciated . I attaching pics.
@stover99
Without more info on the VFD I can't give a definitive answer but looking at your photos I would say the blue wire should be on Vin. Don't take this as gospel.
Provide a copy of the manual and I confirm my guess.
stover99
stover99
Thanks for looking at this. I am attaching the Inverter Manual and additional pics. I have reviewed the manual but unable to make much since out of it. I would like to control my VFD from Masso G3. I am not sure if the jumper cable on the Inverter is set to the correct position for the intended setup. Thanks Steve
  • TB-Woods-XFC-Series-datasheet1-177469416.pdf
@stover99
Ok can confirm my guess was correct but you need to make some other changes as follows.
  • Masso connect 4 -> 6 this provides the -ve connection for REV.
  • VFD move Blue wire to VIN terminal.
  • Wire NO to input on MASSO, configure input as VFD fault - high when VFD in fault.
  • Wire RCM to MASSO Power terminal (red connector)
  • J19 should be jumpered as JBB JB. The first jumper sets the Vin to 0->10v and the second sets the Fwd/Rev to pull down logic, as per section 2.12 on page 23.
  • Parameters 21-MODE = 3 & 75-STR = 1.
There will be other parameters that will need adjusting but I will leave that to you to read up on, infact read all the parameters and make sure you understand what each is doing.