Hi Joshlt,
?
I had a look at your wiring and it looks like you have it wired right but I can also see in your photo that you have not moved the link from VR to VI so it will not take any notice of the speed control from Masso.
The link is on the main circuit board of your VFD beside the 10V terminal on the Right hand side of the Red wire.
Make sure you also check the setting in PD070 as it is set to 5V by default and you will be sending it 10V (It wont hurt it but you will not be able to get the speed correct.)
PD070 |
0 |
Analogue input is 0 = 10V for Masso 1 = 5V for POT on face plate. |
To turn the spindle on first issue a speed command in MDI eg S10000
The on the F2 screen you can click the spindle CW to Start it and the Spindle stop to stop or you can use M3 to start and M5 to stop in MDI if you prefer.
What settings have you put in the F1 Spindle setup screen?
you need to select VFD and enter your maximum speed (probably 24000) as noted on your spindle and I suggest a spin up dwell time of 5000mS and a Spin down Dwell time of 10000mS
It should all work but let us know how you get on.
Regards
Peter