Trying to fire up a Optidrive IP20.
Have wired it as per 3DTEK diagram https://3dtek.xyz/pages/masso-wiring-diagrams
And as per Invertek manual https://inverterdrive.com/file/Invertek-Optidrive-E3-Manual
Digital input 1 operates with positive logic with the following input voltage range
  • "1" --- 8v to 30v
  • "0" --- 0v to 4v
Issuing a M3 - CW rotation or M5 stop makes no difference to the input voltage to Digital input 1.
The voltage on DI1 is 13.7v with respect to MASSO -ve all the time.
OK I've been following @taylortech on Multicam S2412 CNC and I suspect that the cause of my problem is that the wiring diagram from 3DTEK has terminals 4 & 5 reversed. ie It has 24+ve on 4 instead of 5.
When I go to the shed again I will reverse those two leads and see if that fixes it.
For the Bicton Men's Shed.
yes that could be the reason because current will only flow in on direction through the optocoupler transistor.
bictonmensshed
BictonMensShed
EDIT - Problem solved.
OK. I've fixed the enable wiring, 3DTEK's drawing is incorrect, swapped 4 & 5 and now the VFD is outputting a voltage but the spindle is not turning.
Measured voltages, first with the spindle connected and second with spindle disconnected. VFD is set to generate 50 hz for my multi-meter's AC range.
With respect to ground
  • U - 200 190
  • V - 145 190
  • W - 145 190
Between
  • U-V - 44 115
  • U-W - 42 90
  • V-W - 26 115
Measured resistance across all coils is 2 ohms.
So the question is which is faulty? Neither
Does anyone have suggestions? Had to set a parameter to use V/F mode.
Quote from MASSO - Support on November 5, 2018, 7:49 pm
Have you set all the parameters on the VFD to take analog voltage input as control method?
Yes, I spoke to Ben at 3DTEK and we went through all the parameters that needed to be set, I had missed one of the advanced parameters.
He also said that the voltage differences that I measured was normal, when the VFD is not set correctly.