between the -v connections
Consider the power supplies as have two parts the AC side and the DC side, you connect the AC side as per your local electricity laws, on the DC side you need to have a common point between all PSs so that the electric current can return its source and this is the -V terminals.
So for the alarm system to work you have +24v current starting from the 24v PS going into MASSO G3, out of the G3 power terminal, through the resistor then to the motor. There through the motor internal alarm circuit and out the negative power wire to the 36V PS negative terminal, now at this point it needs to get back to the 24V PS, that is where you connect a -V terminal of all PSs together.
Most common arrangement for managing power supply connections is to use DIN rail terminal strips, such as this.
A connector strip is fitted to the top of each group of terminals to make them a "common" block of terminals.
It is better to use these terminal strips to provide power to your peripheral devices than the power terminals on the G3.
Less chance of damaging the G3 if a wiring mishaps occurs.